165 Halsey recurring power issues
Joe Maimon
jmaimon at jmaimon.com
Wed Nov 1 02:51:13 UTC 2023
Willing to bet that there was slicing on both sides of that conversation
and this is what I will now refer to as the expected and resulting razor
burn.
Babak Pasdar wrote:
> Thanks James,
>
> At signup we asked for N+1 power, two circuits to different UPS units.
> I think they sliced it thin by connecting us to two battery packs on
> the same UPS. When the UPS controller crashed both battery packs went
> down. Which now raises the question -- is it reasonable to have to
> specify and expect that two UPS units means that they do not share any
> common points of failure.
>
> Is the UPS the battery or the battery and controller combined?
>
> Babak
>
>
>
> On 10/23/23 15:16, James Jun wrote:
>> On Mon, Oct 23, 2023 at 10:38:09AM -0400, Babak Pasdar wrote:
>>> I wanted to get some feedback as to what is considered standard A/B
>>> power setup when data centers sell redundant power.?? It has always
>>> been
>>> my understanding that A/B power means individually unique and
>>> preferably
>>> alternate path connections to disparate UPS units.
>> Generally speaking, the definition of A/B has become muddied in
>> recent decades. It has almost become an inaccurate marketing term.
>>
>> Most sane people have the opinion (myself included) that when "A/B"
>> power is offered, it is at minimum offererd as 2N UPS (different
>> building entrance and MSBs and even physically separate UPS rooms are
>> also desired on a true 2N A/B, but may not always be available).
>> Some data center operators go even further and architect load
>> switching within their distribution, thereby preventing
>> single-side/one-leg power outages for customers during most of their
>> power maintenance activities
>>
>> Some data center operators treat "A/B" as convenience for them to
>> undertake maintenance and offload uptime responsibilities to their
>> own customers, and require them to either undertake their own
>> transfer switching and/or dual-cord every equipment, so that they can
>> keep taking one side of the power system down for repeated
>> maintenance. This does not scale well for retail colo, as not every
>> customer is going to be good at maintaining two PSUs for every single
>> piece of equipment.
>>
>> Some data centers also view "N+1" system deployment at the UPS as an
>> acceptable form of A/B protection, as long as customer circuits are
>> on different PDUs.
>>
>> Long story short, whether you're receiving N+1 or 2N or 1N, it's
>> important to inquire about how your power circuits will be
>> architected and delivered by the data center, and either have that
>> codified in the contract or reflected appropriately in SLA offering.
>> There is nothing wrong with the data center providing N+1 or 1N
>> power, as long as they're transparent about it and that it is what
>> you're willing to accept for the right terms. However, simply
>> accepting "we are providing you A/B power" or "we've never had
>> primary power failure" are not sufficient to meet proper due
>> diligence during a site selection process, unless you can accept the
>> site outage occurring from time to time, or you're deploying your own
>> power plant (i.e. DC power and batteries) to supplant data center's
>> own power protection scheme.
>>
>> James
>
>