UPS and generator interaction?
Mike Lewinski
mike at rockynet.com
Mon Mar 29 18:53:41 UTC 2004
Brian (nanog-list) wrote:
> Does anyone know of a way to get a UPS to trigger a generator to start, and
> to switch over to the generator power automatically or does this type of
> thing just not exist?
What Patrick said.
But, on a minor note that probably won't affect your Symmetra but I'm
posting in case anyone else here can shed light on.... we had a power
event this AM. The transfer switch did it's magic and all was good...
Except for two new APC1400's- they failed once the batteries drained. I
triple-checked that they were on the right panel, played with
sensitivity, even tried daisy-chaining one off a good working 2200.
Nothing I did would convince the two 1400s they had power. Once the
house power was restored they came back to life and look normal. I later
learned that two of our colo customers with APC1400s had the same
problem :( Other models (even a couple non-essential lower-end, dumb APC
450s and 650s) didn't blink at the generator power.
Mike