MAE NY?
Geoff Lisk
glisk at digisle.net
Wed Oct 7 05:27:36 UTC 1998
I've had really good luck with a very large hole underneath the cabinet and
a several hundred CFM fan at the top. Telehouse has good underfloor
pressure so the larger the hole the better for the cabinet. I haven't had
good luck putting vented tiles behind - most of our equipment vents front
to rear inside the cabinets. My routers are very happy with the large
holes though:
card inlet hotpoint exhaust
RSP(2) 18C/64F 23C/73F 21C/69F
Although after seeing the rats nest of wires in some of the cabinets I've
seen over the years it's no wonder there are hotspots - nowhere for the air
to go. ;)
-Geoff
At 08:10 PM 10/6/98 -0400, TTSG wrote:
>Also make sure that there is a "vented tile" inback of your cabinets.
>Not every one I see there does. Just put in a work order to the
>CAC and they'll put them behind your cabinet. This should help with the
>air flow around the cabinet so the air pumped out has somewhere to go
>(Or help blow into the back vents)
----------------------------------------------------------------------
Geoff Lisk Phone: 415-228-4170
Network Engineer E-mail:glisk at digisle.net
Digital Island Pager: glisk at airnote.net
One hop to the world... www.digisle.net
----------------------------------------------------------------------
More information about the NANOG
mailing list