<div dir="ltr"><div dir="ltr">> Server PS maximum input wattage is 900W.  Present draw of 2.0A @ 208V is <br><div>
~420W, so 420/900 = 46.67%</div><div><br></div><div>But in the real world an R640 would *never* draw 900W. Even if you were to load it up with the maximal CPU configuration (2 x 125W TDP CPU per socket), a full load of 2.5" 15K spinning drives, maximum RAM, and three high wattage low-profile PCI-E cards, while simultaneously running CPU, RAM and disk stress tests, you might get in the neighborhood of 550-600W under load. <br></div><div><br></div><div>Much the same way that a desktop PC equipped with a nominally "850W" rated active PFC 80+ gold power supply might be powering a motherboard and CPU combo with a high CPU TDP, but total power consumption under stress tests/benchmarks would be nowhere near 850W. That rating exists to ensure that the power supply isn't running anywhere near its max capacity...</div><div><br></div><div><br></div><div><span class="gmail-im"></span></div><div><span class="gmail-im"></span></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Fri, Mar 5, 2021 at 3:33 PM Brian Knight <<a href="mailto:ml@knight-networks.com">ml@knight-networks.com</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">On 2021-03-05 15:40, Eric Kuhnke wrote:<br>
<br>
> For comparison purposes, I'm curious about the difference in wattage <br>
> results between:<br>
> <br>
> a) Your R640 at 420W running DPDK<br>
> <br>
> b) The same R640 hardware temporarily booted from a Ubuntu server live <br>
> USB, in which some common CPU stress and memory disk/IO benchmarks are <br>
> being run to intentionally load the system to 100% to characterize its <br>
> absolute maximum AC load wattage.<br>
<br>
We've got a few more hosts waiting to be deployed that are configured <br>
almost identically.  I'll see what we can do.<br>
<br>
I'm guessing those tests would pull slightly more power than the vEdge <br>
hosts, just because there's not much disk IO that happens on a <br>
networking VM.  These hosts have four SSDs for local storage.<br>
<br>
> What's the delta between the 420W and absolute maximum load the server <br>
> is capable of pulling on the 208VAC side?<br>
> <br>
> <a href="https://manpages.ubuntu.com/manpages/artful/man1/stress-ng.1.html" rel="noreferrer" target="_blank">https://manpages.ubuntu.com/manpages/artful/man1/stress-ng.1.html</a><br>
<br>
Server PS maximum input wattage is 900W.  Present draw of 2.0A @ 208V is <br>
~420W, so 420/900 = 46.67%<br>
<br>
> One possible factor is whether ESXI is configured to pass the pci-e <br>
> devices directly through to the guest VM, or if there is any <br>
> abstraction in between. For non-ESXI stuff, in the world of Xen or KVM <br>
> there's many different ways that a guest domU can access a dom0's <br>
> network devices, some of which can have impact on overall steady-state <br>
> wattage consumed by the system.<br>
<br>
The 420W server has its interfaces routed through the ESXI kernel.  <br>
We're moving quickly to SR-IOV on new servers.<br>
<br>
> If the greatest possible efficiency is desired for a number of 1U <br>
> things, one thing to look at would be something similar to the open <br>
> compute platform single centralized AC to DC power units, and servers <br>
> that don't each have their own discrete 110-240VAC single or dual power <br>
> supplies. In terms of cubic meters of air moved per hour vs wattage, <br>
> the fans found in 1U servers are really quite inefficient. As a <br>
> randomly chosen example of 12VDC 40mm (1U server height) fan:<br>
> <br>
> <a href="https://www.shoppui.com/documents/9HV0412P3K001.pdf" rel="noreferrer" target="_blank">https://www.shoppui.com/documents/9HV0412P3K001.pdf</a><br>
> <br>
> If you have a single 12.0VDC fan that's a maximum load of 1.52A, that's <br>
> a possible load of up to 18.24W for just *one* 40mm height fan. And <br>
> your typical high speed dual socket 1U server may have up to eight or <br>
> ten of those, in the typical front to back wind tunnel configuration. <br>
> Normally fans won't be running at full speed, so each one won't be a <br>
> 18W load, but more like 10-12W per fan is totally normal. Plus two at <br>
> least two more fans in both hot swap power supplies. Under heavy load I <br>
> would not be surprised at all to say that 80W to 90W of your R640's <br>
> total 420W load is ventilation.<br>
<br>
Which is of course dependent on the environmentals.  Fan speeds on our <br>
two servers are 25% for the 260W vs. 29% for 420W, so not much <br>
difference.  Inlet temp on both is ~17C.<br>
<br>
I checked out another R640 heavily loaded with vEdge VMs, and it's <br>
pulling similar power, 415W, but the fan speed is at 45%, because inlet <br>
temp is 22C.<br>
<br>
The TDP for the Xeon 6152 is 140W, which seems middle-of-the-road.  From <br>
the quick survey I did of Dell's configurator, the R640 can take CPUs up <br>
to 205W.  So we have headroom in terms of cooling.<br>
<br>
> In a situation where you're running out of power before you run out of <br>
> rack space, look at some 1.5U and 2U high chassist that use 60mm height <br>
> fans, which are much more efficient in ratio of air moved per time <br>
> period vs watts.<br>
<br>
Or ask the colo to turn the A/C lower ;)  (that moves the power problem <br>
elsewhere, I know)<br>
<br>
Thanks,<br>
<br>
-Brian<br>