Power cut if temps are too high
Mel Beckman
mel at beckman.org
Mon May 27 22:31:55 UTC 2019
Most EPO “mushroom” buttons can be wired either NO or NC.
-mel via cell
> On May 27, 2019, at 3:27 PM, Brian Kantor <Brian at ampr.org> wrote:
>
> I was assuming the EPO trigger is a circuit that is normally OPEN
> and is closed when the button is pushed.
>
> If instead, it is a normally-CLOSED circuit, then you are correct,
> you would want two thermostats that both OPENED when the temperature
> rose, which would typically be HEATING thermostats, not AIR CONDITIONING
> thermostats.
>
> Either method could have been installed; in the computer room I
> worked in, the EPO was a normally-open circuit that closed when you
> hit any one of the buttons placed around the room and at the exits.
>
> Or indeed, if the fire suppression system triggered.
> - Brian
>
>> On Mon, May 27, 2019 at 06:10:49PM -0400, Brandon Ross wrote:
>>> On Mon, 27 May 2019, Brian Kantor wrote:
>>>
>>> A simple air conditioner thermostat wired to the EPO switch.
>>> For safety, wire two thermostats in series so BOTH have to trip
>>> before power is shut off.
>>
>> Admittedly it's been a long time since I worked with basic circuitry, but
>> wouldn't wiring them in series cause the circuit to be interrupted if
>> EITHER thermostat tripped?
>>
>> --
>> Brandon Ross Yahoo: BrandonNRoss
>> Voice: +1-404-635-6667 ICQ: 2269442
>> Signal Secure SMS, Viber, Whatsapp: +1-404-644-9628 Skype: brandonross
>> Schedule a meeting: http://www.doodle.com/bross