It's a pretty normal situation.  even with a 1-2m jumper I see light levels that are well below the maximum rx levels for 10km optics. e.g. the max might be .5 and the actual readings are -1.4 - -2.7. our WDM terminals sit in the the adjacent racks to the pop routers so they're all like that. 

ER/ZR is another matter.

On Oct 19, 2013, at 7:33 PM, Chris Costa <ccosta92630 at gmail.com> wrote:

> What are the opinions/views on attenuating short, 1310nm LR cross-connects.
> Assume < 20m cable length and utilizing the same vendor optics on each
> side of the link.  Considering the LR transmit spec doesn't exceed the
> receiver's high threshold value do you pad the receiver closer to the
> median RX range to avoid potential receiver burnout over time, or just
> leave it un-padded?
> 
> Thanks
> 