cooling door
Paul Vixie
paul at vix.com
Sat Mar 29 18:54:02 UTC 2008
> Can someone please, pretty please with sugar on top, explain the point
> behind high power density?
maybe.
> Raw real estate is cheap (basically, nearly free).
not in downtown palo alto. now, you could argue that downtown palo alto
is a silly place for an internet exchange. or you could note that conditions
giving rise to high and diverse longhaul and metro fiber density, also give
rise to high real estate costs.
> Increasing power density per sqft will *not* decrease cost, beyond
> 100W/sqft, the real estate costs are a tiny portion of total cost. Moving
> enough air to cool 400 (or, in your case, 2000) watts per square foot is
> *hard*.
if you do it the old way, which is like you said, moving air, that's always
true. but, i'm not convinced that we're going to keep doing it the old way.
> I've started to recently price things as "cost per square amp". (That is,
> 1A power, conditioned, delivered to the customer rack and cooled). Space
> is really irrelevant - to me, as colo provider, whether I have 100A going
> into a single rack or 5 racks, is irrelevant. In fact, my *costs*
> (including real estate) are likely to be lower when the load is spread
> over 5 racks. Similarly, to a customer, all they care about is getting
> their gear online, and can care less whether it needs to be in 1 rack or
> in 5 racks.
>
> To rephrase vijay, "what is the problem being solved"?
if you find me 300Ksqft along the caltrain fiber corridor in the peninsula
where i can get 10mW of power and have enough land around it for 10mW worth
of genset, and the price per sqft is low enough that i can charge by the
watt and floor space be damned and still come out even or ahead, then please
do send me the address.
More information about the NANOG
mailing list