Assuming the genset was running under load, how often would the oil
filter need to be changed? Are there any other issues that would need
to be addressed in a sustained power outage? As far as genset
maintenance that is.
Dan
-----Original Message-----
From: Richard Welty [mailto:rwelty at averillpark.net]
Sent: Saturday, April 05, 2003 10:09
To: nanog list
Subject: Re[2]: Looking for advice on datacenter electrical/generator
On Sat, 5 Apr 2003 17:47:33 +0000 (GMT) "E.B. Dreger"
<eddy+public+spam at noc.everquick.net> wrote:
> DL> Date: Fri, 4 Apr 2003 21:26:25 -0500 (EST)
> DL> From: David Lesher
> DL> D) Diesel engines, err Diesel-fueled piston engines, be they 2 or
> DL> 4-cycle, need frequent oil changes.
> I thought it was the exact opposite. Diesel fuel has much better
> lubricity than LPG/CNG/gasoline.
diesels need frequent oil filter changes because they load the oil up
with soot. the oil itself can last a long time.
richard
--