32 Old Slip AC Outage and 60 Hudson Verizon failure

Vincent J. Bono vbono at vinny.org
Wed Sep 12 13:28:24 UTC 2001


Status:

We are at 32 Old Slip on the 4th floor.  AC power is down and our generator
air intake is clogged and the sensors shut it down.  Batteries are fine (we
have 27 hours left) but the HVAC is on generator only.  Since we are south
of 14th street we are awaiting permission to enter the area to effect
repairs.  Luckily our staff members who were outside during the collapse are
fine which was our main concern.

Sincerely,
GLOBAL NAPS, INC.

Vincent J. Bono
Vice President
Engineering


----- Original Message -----
From: "Robert Boyle" <robert at tellurian.com>
To: <nanog at merit.edu>
Cc: <engineering at tellurian.net>
Sent: Tuesday, September 11, 2001 10:36 PM
Subject: 32 Old Slip AC Outage and 60 Hudson Verizon failure


>
> Our equipment at 32 Old Slip is not operational. This is apparently
> due to AC power failure and an inability to start the generators due
> to ash in the air (this may be a choice as well). Anyone running at
> 32 Old Slip (TCG/Eagle/Focal/GNAPs are the four I know of on the
> fourth floor) on DC power is on battery or offline.
>
> Our POP at 60 Hudson is up with the MFS/WorldCom provided backhaul
> circuit to our 34 Exchnage Place Jersey City location, but all
> Verizon circuits terminating at 60 Hudson are down/down. All MFS/WCom
> circuits seem to be ok so far...
>
> -Robert
>
>
>
>