On Fri, Jul 11, 1997 at 08:39:08PM -0700, Michael Dillon wrote:
> At 8:20 PM -0400 7/11/97, Alex Rubenstein wrote:
> >According to nitrous.digex.net for its mae-west router:
> >
> > card inlet hotpoint exhaust
> >RSP(4) 26C/78F 38C/100F 44C/111F
> ^^^^^^^
> This is the problem. MFS doesn't have proper cooling if the air if the
> ambient air is this hot. It should be no higher than between 15C and 18C in
> an equipment room like that.
>
> ********************************************************
> Michael Dillon voice: +1-415-482-2840
> Senior Systems Architect fax: +1-415-482-2844
> PRIORI NETWORKS, INC. http://www.priori.net
>
> "The People You Know. The People You Trust."
> ********************************************************
Michael, c'mon...
15-18C? 19C is 66F -- that's very acceptable. 15C would be 59F!
In fact, 68F (at 40% RH) is pretty "standard" for most equipment rooms.
We're config'd for a setpoint of 67F +/- 1F and 40% RH +/- 3%.
One of our more heavily loaded 7513s shows at present:
card inlet hotpoint exhaust
RSP(6) 19C/66F 29C/84F 25C/77F
That's right where it should be.
BTW, exhaust temperature above hotpoint (which your stats show) is *not* a
good thing. I'd find out what's going on there -- you may have some kind
of obstruction with the airflow.
--
--