On 10/23/23 15:56, Eric Kuhnke wrote:
> In this case their use of the incorrectly-described A/B was probably
> exclusively to handle the (not extremely rare) instances of rackmount
> server power supply failures, to give each 1U or 2U size machine, or
> rack of blades, two live power supplies with live power feeds. Nothing
> more complicated than that.
And then inevitably the customer will load the rack with dual supply
gear to the point that each feed is pulling over 50% of the breaker rating.
When one of the feeds eventually does have an issue, they'll immediately
pop the breaker on the other one.
--