Real world power consumption of a 7604-S or 7606-S

Eric Kuhnke eric.kuhnke at gmail.com
Tue Jun 28 00:35:05 UTC 2016


Yes, very much agreed, part of the reason why I'm looking to do the watts
per linecard calculation is to illustrate how it's not healthy except in
certain places. As an edge aggregation device in a very small city in a
rural western US state where the electricity is 6 cents/kWh, the 24x7 load
from a 7604 that eats 950W with supervisors and a 6724SFP linecard is not
so terrible. In this case the colo space for a 42U rack is sometimes
literally free.

In a IX point/datacenter/colocation environment where rack and power costs
real money, not so much.


On Mon, Jun 27, 2016 at 5:26 PM, Tom Hill <tom at ninjabadger.net> wrote:

> On 28/06/16 00:26, Eric Kuhnke wrote:
> > Example:
> > 7604S chassis with dual 2700W DC power - chassis and fans use how much
> > power?
> > 2 x RSP720-3CXL at 310W each
> > WS-X6704 with DFC4 - ???W each
>
> Way too much, is the simple answer.
>
> I did have a 7604 (non-S) with the same PSUs, 1x SUP720-3BXL, 1x
> WS-X6724-SFP and 1x WS-X6708-3CXL was drawing near 2kW.
>
> It's not healthy, please consider how much you'll spend in electricity
> vs. something else. For example, the ASR9001 uses a 5th of the power.
>
>
> Cisco do also have a power calculator, too. It's conservative but not
> overly so:
>
>  http://cpc.cloudapps.cisco.com/cpc/launch.jsp
>
> --
> Tom
>