> I worked in a data center with something I thought was very, very cool.
>
> http://www.hilkar.com/highresistance.htm
>
> The concept, at a high level, is rather than tie the (service, not
> signal) ground back to grounding rods directly you run it through a
> large resistor. Now when a phase is "grounded" it runs through the
> resistor, allowing a small but safe current to flow.
>
> Why is this cool? Well, say you have a power strip running at 10A
> with a bunch of servers on it. If you took a paperclip and inserted it
> in an empty plug connecting hot to ground with a normal system
> (simulating a faulty bit of gear) the breaker would trip, all your
> servers would go off.
>
> If you did this with a high resistance setup the paperclip would conduct
> about 0.5A, maybe less. An alarm, dectecting current, at the resistor
> would go off to say there was a fault. Your circuit would draw 10.5
> amps and everything would stay up and running. That faulty bit of gear
> didn't take down your entire power strip.
>
> This totally eliminates arc faults, and there isn't enough current to
> ground to arc. I think GFCI's are also unnecessary, as the fault can't
> conduct enough current to be harmful.
All is "well and good", *UNTIL* "something happens" that introduces _another_
path to 'ground' that bypasses the 'high rresistance' links.
(Reminiscent of the old "Branch on C.E. grounded" programming joke.)