Want to move to all 208V for server racks

Ingo Flaschberger if at xip.at
Thu Dec 2 21:46:19 UTC 2010


> It is probably worth nothing that a 3-phase input in Europe is actually 
> 240/415 volt Y (for every panel I have seen in Germany at least, even 
> the places I have lived there had 240/415 three phase).  The normal 240v 
> single phase outlet circuits were the phase to neutral voltage. 
> Obviously Europe also runs at 50 hz vs 60 in the US as well but the 
> three phase still works the same way.
>
> A Europe 64 amp 240/415 circuit is pretty close to equivalent in to a 
> 277/480 Y configured 60 amp circuit in the US.  The biggest notable 
> difference is that equipment that runs on two different service voltage 
> ranges where Europe has far less need for in-building step-down 
> transformers since even small loads work on the phase-to-neutral voltage 
> of the big services.  I always find it interesting in the US to note how 
> many 480v to 120/208Y step-down transformers one can find in a big 
> building or datacenter.
>

aeh.. 230V / 400V is right voltage in technical terms in most european 
copuntries.
(years ago it was 220V / 380V, before it was decided to go up with the 
voltage)

and in bigger datacenters there are also step down transformers from 10kV 
down.

Kind regards,
 	Ingo Flaschberger