Operate until failure

Dalvenjah FoxFire dalvenjah at DAL.NET
Mon Jan 8 23:35:19 UTC 2001


On Mon, Jan 08, 2001 at 02:35:49PM -0800, Sean Donelan put this into my mailbox:
> One issue with highly redudandent data centers is the failure modes are
> "interesting."  You don't want to shutdown due to a single UPS failure, so
> you don't use something simple like PowerChute Plus.  You most likely don't
> want to shutdown based on any automatic signal.  However, you do want a way
> for an operator to gracefully shutdown a lot of equipment quickly when
> the decision is made.

It should be technically fairly easy to set up an
'Emergency Graceful Shutdown' button to live next to the EPO button; this
controls a line that runs through the data center that activates either
one relay per system or one optoisolator per system, depending on your
fancy, that can raise or lower a particular serial line (DSR, CTS,
whatever). You then install a daemon (again, fairly simple) that
listens to this serial line; when it detects a change, it executes a
graceful shutdown on that system.

If you wanted to get fancy, pushing the "EGS" button could send a series
of pulses that the daemon would have to interpret; this way you guard
against odd line noise or loose connections triggering the shutdown. You
could even set up a 'Cancel EGS' signal, as well.

You could then interface this to more stuff, like the "You'll be out of
diesel for your generator in 120 seconds" alert, etc. etc.

Then again, my sprinklers water my lawn via a cron job, so I might just
be Different.

-dalvenjah 

-- 
 Dalvenjah FoxFire (aka Sven Nielsen) "If her breath were as terrible as her
 Founder, the DALnet IRC Network      terminations, there were no living near
                                      her; she would infect to the North Star!"
 
 e-mail: dalvenjah at dal.net             WWW: http://www.dal.net/~dalvenjah/
 whois: SN90                           Try DALnet! http://www.dal.net/